I am interested in three tests used on the insulation systems; both stator and rotor windings.  These test are the Poalrization Index, Dielectric Discharge and Step Voltage.  I have used PI testing on my generators forever and am considering adding both Dielectric Discharge and Step Voltage to our maintenance program.  The few times I have perfromed these 2 test they have produced wildly different results for sister units and non-related units.  Especially, between different rotor windings.

I am looking for a detailed discussion of how the results are to be evaluated and how results differ over time and between stator/rotor windings.  In addition, are the results affected (and how) by surface contamination, temperature or humidity?  Are the reults trendable?

Any information or references would be greatly appreciated.

RE: Generator Insulation Testing

I have been using these tests for some years now. I find the DD test to be more or less in line with PI. In some slow speed motors, I have been getting high DD values for years & the winding seems to be fine. Tan delta values are good, took the motor apart, did not see anything. Found contaminated motors with DD too, where DD improved later.

Which step voltage are you referring to? Some companies test the winding at five different voltages & plot IR vs. voltage. I never found this useful.

Others apply DC voltages in steps to cross the operating voltage, measuring the leakage current at each point. If the knee point is above the operating voltage, the machine gets accepted. This does give some trendable results.

Regards,

Aditya    

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources