in New York City, can a wire (say 12-3) be located in an electrical distribution panel but not be connected to a circuit breaker ? In other words, keep it there for future use?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
future use wire in panel
|
future use wire in panelfuture use wire in panel(OP)
in New York City, can a wire (say 12-3) be located in an electrical distribution panel but not be connected to a circuit breaker ? In other words, keep it there for future use?
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: future use wire in panel
Good Luck
RE: future use wire in panel
The NEC does not prohibit splices in panles. See 312.8 in the NEC.
Don
RE: future use wire in panel
You are correct that althought the 2004 version of the code states that the enclosure shall not be used as a junction, pull or gutter for through feed conductors, it does allow for splices and taps if the percentage fill requirements are met. This is not in the code being enforced in my locale as we are on the 2001 code, (which goes from section 310 directly to 318), with 2004 State revisions. We will be moving to the 2004 with 2006 revisions shortly-so that may change.
I maintain however that this is poor practice and would not recommend this as a standard for installation. I do not know specifically what the New York City Electrical Code allows, or which edition of the NEC they have adopted. I do know that the city code, like the California State Code we use, utilizes a version of the NEC with numerous revisions which may impact this installation. Our specifications do not allow this, and we will retain that provision even if the new code allows it. My recommendation to stevedantonio, is still to check with the AHJ and run this past them. I would be interested to know what the City tells him.
Good day and good luck.
RE: future use wire in panel
In January 1, 2004 went in effect the Local Law 64/2001 to amend the administrative code of the city of NY , in relation with the NEC (NFPA-70). Presently, the electrical code revision committees are reviewing the 2005 NEC and drafting additional amendments to apply locally.
Sections 310 directly to 318 do not have amendment. Therefore, NEC 2004 in this area are acceptable as applicable standard.
RE: future use wire in panel
Thank you all for your help.
RE: future use wire in panel
Those must be local codes as the dates for the NEC are every three years. Your code may be based on an older NEC. The articles in Chapter 3 were rearranged in the 99 or 02 code. Take a look at the exception to 373-8 in your code. The basic wording has been the same for many code cycles, although, the exception has been rewritten in positive code language per the NEC style manual.
Don
RE: future use wire in panel
JTK
RE: future use wire in panel
RE: future use wire in panel
Mike
RE: future use wire in panel
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
RE: future use wire in panel
I don't see any electrical or safety problems with your suggestion. I would probably do exactly as you suggested.
However, if an inspector said,
"That doesn't meet the code. Please change it", I would change it.
I assume that stevedantonio's post that starts "NYC has told me", refers to the NYC inspection department.
If so, then I consider stevedantonio's post to be the correct and final answer.