Galvanized anchor bolts
Hello
We are converting the CO2 Removal Section at our Ammonia Plant from conventional Benfield system to Benfield LoHeat System. Anchor bolts of material ASTM A307 will be installed on heavy steel structure, carrying a load of 350 tons.
The supplier has offered hot dip galvanized anchor bolts; previously we have always used bare anchor bolts (w/o any coating).
Is it all right to use hot dip zinc plated anchor bolts in concrete foundations or there are some areas of concern that need to be evaluated/ controlled during fabrication of anchor bolts?
RE: Galvanized anchor bolts
A325, A307, F1554 etc can all be HDG no problem. If setting in concrete you are much better off with galvnanized bolts rahter than bare anyway.
Using galvanized bolts inside concrete is not an issue. When you say hot dipped galvanized; what is the coating thickness in microns? You'll have to pay attention on this. Because, when you use galvanized anchor bolts in a aggresive environment, there is a rate of removal of the coating. If your coating is not enough, you'll be ended up with a difficult situation. Ask for "Sheradised" which has a coating thickness of approx. 43 microns or specify the galvanized thickness.
Dik