Hi guys can you tell me the difference between testing motors between IEEE 112 Method F & F1

RE: IEEE 112 Testing

Hello magnetited,

In North America the electric motors are tested in accordance with IEEE 112, But you can find this methods: B,C,E,E1,F and F1.

In The F method is not neccesary to couple up the motor and a is necesarie to perform a Dual-Frecuency heat run and use
stray loads.

The F1 method use an assigned value to the load loss.  

Regards

Petronila.

 

RE: IEEE 112 Testing


Basically in Method F, Stray Losses are measured, and in Method F1 are calculated or assumed!

Is that correct?

RE: IEEE 112 Testing

Both are Test Methods for Efficiency based on calculation of the performance at various loads by solution of the equivalent circuit.
As Tommy007 said; On method F the stray-load loss is directly meassured. For method F1 stray-load loss is assumed

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources