VFD with multiple fan motors overcurrent protection

VFD with multiple fan motors overcurrent protection

VFD with multiple fan motors overcurrent protection

(OP)
I know the the overcurrent protection line side needs to be fast interrupt. What is the concensus for overcurrent on the load side with multiple fan motors.
Any concerns for multiple motors on single drive

Any help appreciated.

RE: VFD with multiple fan motors overcurrent protection

You should have overload protection on each fan. The drive overload only protects the drive output and not the load, in your case.

RE: VFD with multiple fan motors overcurrent protection

Slight correction, you MUST have OL protection for each individual motor downstream from the VFD.

Eng-Tips: Help for your job, not for your homework  Read FAQ731-376

RE: VFD with multiple fan motors overcurrent protection

Be careful about using manual motor starters. The switch, breaker and overload all-in-one type of controller. Many of them will overheat on the output of a VFD. The ones I've seen have problems had a coil inside for the instantaneous overcurrent trip and that coil overheated.

RE: VFD with multiple fan motors overcurrent protection

LWFB,

I would suggest that you choose OL relays so that the motor FLC is roughly in the middle of the adjustment range. There will be losses in the cables associated with the VFD PWM frequency and you may need to adjust the 'overload' protection for a little over the motor FLC to allow for that.
Please be aware that 'Instantaneous Overcurrent' - short circuits between phases or phase to earth - will not be protected against. The VFD will be much quicker at tripping (or at least should be!) than the relay opening when this kind of fault occurs. I believe it will be very dificult to find a relay that will trip on Instantaneous before the drive trips.
So this will mean that if one of your multiple motors or their cables has a short circuit fault then the drive will trip and all the motors will stop. Normally, this is rare! It will depend on your application.

Drivesrock.

RE: VFD with multiple fan motors overcurrent protection

Quote (LionelHutz):

Be careful about using manual motor starters. The switch, breaker and overload all-in-one type of controller. Many of them will overheat on the output of a VFD. The ones I've seen have problems had a coil inside for the instantaneous overcurrent trip and that coil overheated.
I have seen this too, but to be honest, the problem goes right away by simply putting a load reactor on the VFD output side (in front of the motor protectors), which has additional benefits when using multiple motors such as helping to protect the VFD from short circuits in the load wiring.

Eng-Tips: Help for your job, not for your homework  Read FAQ731-376

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources