When installing a bank of utility transformers, say 100kVA 25kv:277/480V, using three single phase transformers, what effect does unmatched impedance have on the operation of the bank?  If one transformer is 2.0% and the other two are 1.6% for example, what will this do?

K2ofKeyLargo

RE: three single phase transformers impedance matching

You will get unmatched fault currents and unmatched voltage regulation.

RE: three single phase transformers impedance matching

The transformer bank with unmachet impedance can not be loaded a full capacity.

RE: three single phase transformers impedance matching

Doesn't this depend on the type of hookup? I was under the impression from some old REA transformer guidelines that the only bank that really had to be watched on this was from a delta/delta connection. I understood that in wye/delta and wye/wye banks it wasn't that much of a concern.

RE: three single phase transformers impedance matching

Fault current; Divide the full load current by the %impedence to get available fault current. As long as it's less than you equipment rating no problem. If you can safely use three 1.6% transformers, you can use one 1.6% with two 2% transformers.

Voltage regulation.
277 x (1. - .02) = 271.46 volts
277 x (1 - 1.6) = 272.568 volts
difference,     = 1.108 volts
One phase will run 1.108 volts higher than the others, the rare time that the incoming phases are exactly equal voltage.
I wouldn't worry.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources