Horizontal Recirculator Capacity

Horizontal Recirculator Capacity

Horizontal Recirculator Capacity

(OP)
Does anyone know how to determine the max capacity of a horizontal recircualtor package that's 60" x 18', operating at -35 degees F, with a 4:1 recirc rate and wet return connections on opposite ends of the vessel.  The refrigerant used is NH3.

RE: Horizontal Recirculator Capacity

(OP)
I've tried Evapco's RVS catalog and Frick's as well, but their vessels aren't nearly as long as the one that we have.

RE: Horizontal Recirculator Capacity

I think you will find the diameter pretty much controls the size for a specific capacity.  The length is added for surge or liquid volume.  You can find the sizing criteria in the ASHAE Handbook.

I'd give you an approximate number, except we are moving and all of my data boks are on a moving truck.

Ken

TXiceman
www.rae-corp.com

RE: Horizontal Recirculator Capacity

Charts for Determining Rate of Refrigerant Feed
(No Flash Gas)from ashrae is 0.059 GPM or 0.0575 lb/min at
-35 degreesF 2002 ASHRAE Refrigeration Handbook page 1.4

RE: Horizontal Recirculator Capacity

Imok, check your last post, the 0.0575 can't be right.


The Separation Capacity of a horizontal vessel is going to be very much the same for any 60" Diameter, from any manufacturer, until the pump requirements kick into the equation...So if a reputable manufacturer constructed the package intact and knew its refrigerant, temperature and operating requirements, it will be tall enough that the (original) pumps will have sufficient NPSH at a specific, maintained operating level.  An it won't vary much from manufacturer to manufacturer.  If the pumps have been renewed and upsized, or if the pump inlet piping was designed with a higher evaporating temperature intended, or if operations require that the liquid level be otherwise run "high", the separation space is being encroached upon...

Providing the pumps have enough flow and pressure, the answer for a purpose-built package should be about 425 TR.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources