Condenser/Hotwell Air Inleakage Testing

Condenser/Hotwell Air Inleakage Testing

Condenser/Hotwell Air Inleakage Testing

(OP)
I am currently trying to determine the location of air ingress by spraying Helium at suspected leak locations and measuring the amount from the Vacuum pump discharge.  Is there a better way of performing this check on locations that are below the water level?

RE: Condenser/Hotwell Air Inleakage Testing

Maybe. During an outage , drain the condenser hotwell, and use an ultrasonic noise generator and sensing microphone. However, this will not pickup leaks that may be caused by cracks that have opened up  due to on line forces, such as weight of condensate or vaccuum forces.

RE: Condenser/Hotwell Air Inleakage Testing

Generally, the only good ways are the following:
1.  Helium/ SF6 gas testing.  In the old days we were able to use Freon - till the greenies complained about the ozone layer.  This method works well, but takes a long time to complete.
2.  Flood testing.  During an outage, fill the condenser with water, and look outside for any leakage.  Just a warning that some condensers are not designed to carry a full volume of water without having supports installed - chek with your OEM.  Also check around your LP heaters and HP heaters if they have a vent to condenser.  Many problems arise from this area.
3.  Ultrasonic leak testing on a power plant to try and find leaks on a vacuum system do not work.  Generally the background noise is just too bad.  
4.  Always try to distinguish between above and below the water line.  Generally leaks below the condenser normal working level is associated with an increase in condensate dissolved oxygen, whereas leaks above the water line is not.  
5.  Never trust your chemist - always have them check their oxygen analyser with a test sample before you cart all the equipment to site.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources