How many splice are allowed in a single length of 35kv cable

How many splice are allowed in a single length of 35kv cable

How many splice are allowed in a single length of 35kv cable

(OP)
we have four gas turbine generators , two are located on other side of the fence , all four will be tied to gether through 35kv,35okcmil,2nos cables length around 1.5kms , there are three splices per cable , wanted to know how many splice are allowed in a length.

thanks

lucky

RE: How many splice are allowed in a single length of 35kv cable

I don't think there is a limit by code etc, but minimizing them is always good.

However, practically it is difficult to get single length of cables in excess of 250 or 300 meters. So you can expect a splice every such distance. So from that point of view 3 splices in 1.5km run is pretty good.

The splices should only be in manhole or a hand hole or in accessible and protected space.

RE: How many splice are allowed in a single length of 35kv cable

I often found that the joint itself is the strongest point within the HV Line (if properly done, of course...!).

The limitation of joints in a line is due mainly to an increased possibility of human errors when doing the joints...

Verify that the semiconductor materials are properly repaired, that screens are countinuously sounds and that external armors are well joined and protected. Use a crimping tool for the barrels that will make a round pressure and verify that the cores are well inserted within the barrels. Then make a proper High Voltage pressure test. That's the best you can do.

By the way, if joints are made with proper waterproof compound, they could be directly buried, but a clear mark shall be installed on the soil surface clearly indicating the position of the joint.

After all the above, record everything in a Log Book (generally an O&M Manual) and move on.

Best luck.

Giuseppe

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources