Dissipation Factor Tests

Dissipation Factor Tests

Dissipation Factor Tests

(OP)
I have been doing tan delta testing of motors for many years now. While there are standards for new coils, I am yet to come across any standard for the complete motor. Also, never seen any limiting values for old motors. Does anybody have some references?

Regards,

Aditya  

RE: Dissipation Factor Tests

Doble has a large database of rotating machine power factor tests.  It's available to those who rent Doble analysers.

I'm in the middle of a move and stuck away from my references.

Doesn't IEEE286 address complete motors?

I think some more repair specs may specify general power factor limits for assembled motors: EPRI 1000897 (available to EPRI members), ANSI spec for power plant motors, possibly EASA AR100?

As you know the power factor and tipup results can be difficult to interpret for 6kv and above due to presence of end winding voltage grading tape/coating which cannot be guarded out while testing assembled motor.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Dissipation Factor Tests

(OP)
Hello Electricpete,

Thanks for the lead. I was able to purchase the IEEE standard on-line. I went to the EASA website, could not find the AR100 document anywhere. Do you have a link?

Based on the other material I have been collecting & my field experiences, I have some opinions. Would like to hear your views:

1. High tan delta could be due to either moisture, aging or improper consolidation of the insulation.

2. High tan delta tip-up is indicative of voids in the insulation.

3. High capacitance tip-up is indicative of partial discharges.

4. Negative tip-up is indicative of grease or oil contamination.

Regards,

Aditya

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources