Current Transformer Test for Insulation Resistance

Current Transformer Test for Insulation Resistance

Current Transformer Test for Insulation Resistance

(OP)
Dear All

Our client have  36kV current transformers in the switchgear.Due to some airconditioning issues, there was moisture discovered in the cable section.The CTs had visible signs of oxidation and paths of corona discharge.They tested for insulation resistance of primary winding with respect to earth with CT secondary connected. The value was 55M ohms. Until that day the CT were in operation. Is this an accepatable value.OR is this test acceptable to determine whether to continue operation. Any time saving suggestions?

Thanks in advance.

RE: Current Transformer Test for Insulation Resistance

Sir,
55M ohm at what voltage was the test conducted? Were any other tests carried out?

RE: Current Transformer Test for Insulation Resistance

Assuming the test was carried out at 1 kV or higher, I would sat 55 MOhm is ok.

I would also check pri-to-sec and sec-to-ground

RE: Current Transformer Test for Insulation Resistance

(OP)
It was done at 1kV.

RE: Current Transformer Test for Insulation Resistance

If I understand this correctly, the CT was meggered on the primary side (36kV) at 1kv (assuming dc) and a value of 55Mohm was recorded.

Two problems. One if you did perform the test on the 36kV side. 1kv is to low of a test voltage for valid results. The test should of been conducted at 15kVdc or higher. You could also contact the manufacture for a test value and there recommendation on minimum insulation resistance.

Second, the 55Mohms is very low insulation resistance. 600volt equipment recommended minimum insulation resistance is 100Mohms. If you want to use that for a base then the CT should be replaced.

All the above values are from NETA Maintenace Testing Specifications.

Good Luck

RE: Current Transformer Test for Insulation Resistance

To me 55M is okay, afterall they were in service  along.What i think should happen is to cleanout the oxidation and make sure moisture does not get in there again.With time it will improve to higher value.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources