Under Floor Air Distribution
Under Floor Air Distribution
(OP)
Has anyone found a software program (or other method) that will calculate cooling loads in the occupied zone using an underfloor air distribution system?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Under Floor Air Distribution
|
RE: Under Floor Air Distribution
Many are having good luck with the round, high-velocity swirling nozzles. They seem better suited to underfloor distribution in high-occupancy environment. (As opposed to the classic perforated floor tiles in a computer room.)
Here's Titus's version:
h
This is also a great general article about the subject:
htt
RE: Under Floor Air Distribution
This seems to be the consensus on designing UFAD systems and I will proceed until a software program is developed to accurately take into account the temperature stratification of the UFAD.
RE: Under Floor Air Distribution
http://www.cbe.berkeley.edu/underfloorair/
The basic logic is that the air supply to the space is calculated using an "adjusted" amount of people and equipment loads (and other cooling loads) to allow for part of the room heat gains to be stratified and drawn off into the return air side. The heat from lights is not a "space load" since it is removed by the return air path. The actual AHU cooling coil load, however, has to be enough for ALL of the total heat gains being extracted form the room. The actual supply air to the room is usually around 65% to 85% of what you'd normally use for a conventional overhead system. CFD modeling will provide a better analysis of the room loads and air temperature stratification.
RE: Under Floor Air Distribution
I'm a little surprised that the air flow is that much less than a conventional system. I realize that the loads are less due to stratification, but I thought the higher supply temperature balanced that out and made the airflows close to the same.
RE: Under Floor Air Distribution
________________________
1.08 x (Room Temp - ADP)
As the room sensible heat reduces, the air quantity also will obviously reduce. The room sensible heat would reduce, eventhough the total heat is not reduced, if you are able to get the heat to be dissipated through the return air - In other words, it becomes part of the coil load, but is NOT part of the room sensible load.
Example - Heat dissipated by lights above a false ceiling which is used as a return air plenum.
I have also not come across any special software for underfloor cooling load calculations.
HVAC68
RE: Under Floor Air Distribution
With respect, you asked for "calculating cooling loads", not airflows. Neither did you ask to do a coil selection, determine ventilation rates, or calculate the sensible heat ratio. Space/zone loads differ from total load, as GMcD points out, but you did not ask that question, either.
Please note that my reply was also the first to include Mr. Bauman's link, as well. There's a lot of selective reading vs. selective writing going on, apparently.
RE: Under Floor Air Distribution
I thought the intent of this website was to generate a dialogue between professionals and share ideas, not to see who is the smartest. Unfortunately dialogue through the written word doesn't carry the same personal depth that the spoken does. I aplogize for inadvertantly hurting your feelings.
RE: Under Floor Air Distribution
my mistake entirely ... please forgive my obtuse sensitivity