Resistance VS Reactor Grounding
Resistance VS Reactor Grounding
(OP)
Hi all! Most of the time, we use a resistance grounding on transformers to limit the line to ground fault current.
But yesterday, I have tested an oil transformer that was using a reactor on the X0. In my short experience in power
systems, I have seen many generators 13,8 kV grounded via a reactor but not a transformer. That xfo is a 50 Mva, 120 to 2.3 kV. Why using one type of grounding over the other?
Thank!
But yesterday, I have tested an oil transformer that was using a reactor on the X0. In my short experience in power
systems, I have seen many generators 13,8 kV grounded via a reactor but not a transformer. That xfo is a 50 Mva, 120 to 2.3 kV. Why using one type of grounding over the other?
Thank!






RE: Resistance VS Reactor Grounding
Resonant grounding (Petersen Coil or Arc suppression coil)
It is a tuneable reactor connected in the transformer neutral to earth. The value of the reactance is chosen such that reactance current neutralises capacitance current. The current at the fault point is theoretical nil and unable to maintain the arc, hence the name. Normally used on systems above 15kV.
Low inductance grounding.
Normally reactance grounded systems is rarely used due to problems with overvoltages under arcing earth fault conditions, and the fact that the desired level of fault current higher is than the same size resistance grounded system. Therefore reactance grounding is usually not considered an alternative to resistance grounding.
However, to achieve the same value as the resistor, the design of a reactor is smaller and thus cheaper - maybe a possible option to use it.
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
RE: Resistance VS Reactor Grounding
There are other engineering uses, but as always, price is a major factor.
JTK