Anchor design

Anchor design

Anchor design

(OP)
Question is about supplementary reinforcement suggested by ACI. This is for a column supposed to be "Fixed" to foundations.Axial load is 16870 lbf(uplift) and moment is 155413 lbf.ft. Using a baseplate 20"x20"x1 5/8", I need 10/12 Nos.
1 1/8" dia bolts and also need about 18" of embedment depth.
The pier size is restricted to about 24". Full breakout
capacity of 35 degree  prism can not be mobilised because of close spacing. ACI says that calculations for breakout capacity is not needed if supplementary reinforcement
connecting the potential failure surfaces of breakout prism
to lower parts of structure is provided. Are these supplementary rebars for developing the uplift forces in the
anchor bars ?  If  so then can I compute the bond/development length by using usual equations for bond
length ?

RE: Anchor design

I haven't read that in the ACI, unless it is in the 2005, which I do not have yet.  Would you mind letting me know the section that is in?  What I remember is that you can use a higher phi if you have supplementary reinforcing, but you still have to check breakout.

RE: Anchor design

"Are these supplementary rebars for developing the uplift forces in the anchor bars ?" - Yes.  

The way I normally do this is to provide enough vertical reinforcing in the pier to develop a capacity equal to that of the anchor bolts.  Hook the reinforcing bars just under the top of the pier and then sink your anchor bolts down far enough so that the vertical reinforcing is developed at the depth that the failure plane crosses them.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources