Transformer Bushing

Transformer Bushing

Transformer Bushing

(OP)
I need help to identify the difference between distribution class and power class bushing for power transformer
Thanks

RE: Transformer Bushing

It's been years since I worked with bushings, but if memory serves me right.
There is no difference between a bushing used on a distribution transformer and a power transformer.
The transformer manufacture usually goes through the bushing manufacture's catalog and selects a bushing that meets the mechanical requirements, operating voltage, operating current and test voltages of the transformer being designed.
Since power transformers operate at higher power and are usually tested at higher voltages, bushings used on power transformers tend to be larger than bushings used on distribution transformer.

RE: Transformer Bushing

I'm not sure if distribution class and power class is the correct terminology, but in the USA, typically, bushings on power transformers will be higher BIL than those on distribution transformers.  At 12.5 kV, power transformer bushings are 110 kV BIL and distribution transformer bushings are 95 kV BIL.

RE: Transformer Bushing

Regardless if the transformer is classified as power or for distribution type, the bushings are specified to operate safely within electrical and mechanical withstand values. The main electrical parameters are:
o    Maximum continuous operating current.
o    Basic insulation level (BIL)
o    Creepage distance of the bushing

In polluted environment, the minimum creepage distance may be the driving parameter to avoid flashover. Therefore, larger bushing with higher BIL may be required by the minimum values stipulate in the standards.

Below, is the minimum dielectric insulation level per ANSI/IEEE Std C57 for distribution transformer and Class I power transformers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources