Min. Number of Ladder per Platform

Min. Number of Ladder per Platform

Min. Number of Ladder per Platform

(OP)
We are designing support platform about 23 ft above ground for cooling towers. I am assuming that required number of caged ladder depends on size of platform. Any references? I have searched OSHA w/o success.
Thanks,

Ibro V.

RE: Min. Number of Ladder per Platform

OSHA may not say how many ladders you need(maybe two would be good), but OSHA will say how the ladders will be designed as wel as the platform.

Richard A. Cornelius, P.E.
WWW.amlinereast.com

RE: Min. Number of Ladder per Platform

I'm not aware of a specific requirement either.  Tank roofs normally have 1- ladder regardless of size, for example.

As I recall, OSHA does specify that if used regularly (IE, daily), a stairway should be used rather than a ladder.

RE: Min. Number of Ladder per Platform

Have you looked at NFPA 214?

RE: Min. Number of Ladder per Platform

Means of Egress is discussed in OHSA 1910.35 - 37 (Subpart E).  Design details for ladders is discussed in 1910.27.  If the platform is just for operations and/or maintenance to the cooling towers I would think only 1 ladder is required.  If the platform is part of a route for plant personnel to exit the area during an emergency then the platform is part of the means of egress and I don't think you could even use a ladder, you would have to use stairs.

RE: Min. Number of Ladder per Platform

NFPA-101-2000 (Life Safety Code)sections 7.2.9.1 (3) and 40.2.2.10 allows ladders as a means of egress to platforms whose intended occupancy doesn't exceed 3 people at any one time.

RE: Min. Number of Ladder per Platform

2 is more popular for us if a platform has signifcant sizes (e.g. 20ft or larger), for access and egress purposes. Usually, the number is req'd or determined ay Piping or clients.

In process plants, lots of cases, platforms are interconnected by ladders and stairs, no platform is a dead end.

RE: Min. Number of Ladder per Platform

For a "room" meaning any where more than I think 10 people work requires 2 means of egress, Fire Code.

Richard A. Cornelius, P.E.
WWW.amlinereast.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources