Transformer Zero Sequence Impedance in SKM Powertools
Transformer Zero Sequence Impedance in SKM Powertools
(OP)
Can anyone please offer tips in modelling transformer zero sequence impedance of transformers in SKM Powertools. We mostly encounter three-phase delta-grounded wye units, some of which have neutral earthing impedances installed at the star point.
I have seen information stating none should be modelled, other information stating 90% of positive sequence impedance, and yet other information that making it the same as the positive sequence impedance is acceptable.
Thanks
I have seen information stating none should be modelled, other information stating 90% of positive sequence impedance, and yet other information that making it the same as the positive sequence impedance is acceptable.
Thanks






RE: Transformer Zero Sequence Impedance in SKM Powertools
RE: Transformer Zero Sequence Impedance in SKM Powertools
After searching the forum and further reading, for most of the transformers we deal with (3 phase Dyn, most likely with core-type cores, i.e. not shell), R0=R1 and X0=(0.85 to 0.9)X1 will be suitable (NER values to be added separately).