blower motor power????
2

blower motor power????

blower motor power????

(OP)
guys,,

how can i determine the blower shaft power?

RE: blower motor power????

Look it up?

Meaure current and voltage?

Strain gages on the shaft?

Force transducers on the motor mounts?

Mike Halloran
Pembroke Pines, FL, USA

RE: blower motor power????

(OP)
no i mean a law like in shaft power of
pump=Q(gpm)*H(ft)/pump eff.*3960  

RE: blower motor power????

BHP=(cfm)*(static pressure + velocity pressure{in. of water))/4100    

The above “rule of thumb” will need to be adjusted for fan efficiency.

RE: blower motor power????

HP =      CFM x SP
      __________________
   
       6355 x Efficiency

HVAC68

RE: blower motor power????

HVAC68

I see that you have a different conversion factor in the denominator than I had.  6356 vs. 4100

This will make a big difference.  So, I looked in some references:

“HVAC Equations, Data, and Rules of Thumb” by Arthur A. Bell gives 6356 on page 38

“Air-Conditioning Systems Design Manual” by ASHRAE gives 4100 on page 5-31

I haven’t cranked the numbers to find which factor is correct; however, this just shows how it is important to personally verify these cookbook rules of thumbs.  I will drop a note after I make the calculations to verify which factor is correct.

Regards,
Zapster

RE: blower motor power????

Shaft power is calculated as a product of input power and motor efficiency or H = BE×? motor

Where: H = shaft power (W)
       BE = input power(W)     
       and ? motor = motor efficiency


RE: blower motor power????


The formula for fans' power input is:

HP = (CFM)(in. wg)(K)/(6354×η)

η is the efficiency as a ratio of fan output power to fan input power which includes losses due to skin friction, leakage and mechanical friction.

K is the compressibility coefficient, itself a function of the polytropic exponent, and the absolute total pressures at the inlet and outlet.

As to velocity head, in. wg, it is estimated from the air velocity in fpm, assuming air incompressible, 1 in. wg = 5.193 lb/ft2, gc = 32.174 ft.lbm/lb.s2, the formula is:

in. wg = (V/4005)2
,
The divisor 4005 results from assuminmg dry air at 70oF and a pressure of 29.92 in. Hg with a density of 0.075 lb/ft3. It becomes 4100 when assuming moist-saturated air at 25oC.
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources