How to measure the resistance of the secondary winding of a current transformer at site.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Current Transformer
Julian
RE: Current Transformer
RE: Current Transformer
Julian
RE: Current Transformer
I fully agree with what you say, in terms of the defined external burden that a CT must be able to supply within its accuracy rating (for CTs rated on this basis).
However, there are instances where knowledge of the CT secondary winding resistance is needed. Examples of this are high impedance protection schemes and any application where the transient performance of the CT, as against its steady state performance, must be evaluated.
See Thread238-6198 for more discussion, or check http://www.geindustrial.com/pm/notes/ger3973.pdf
RE: Current Transformer
Julian
RE: Current Transformer
RE: Current Transformer
By the way. Most of CT, exceeding 100 A as primary nominal current, have not primary winding as they are of the pass-through type.
Julian
RE: Current Transformer
230842/Julian - I actually said that the CT primary should be OPEN circuited, precisely for the above reason.
RE: Current Transformer
RE: Current Transformer
RE: Current Transformer
RE: Current Transformer
You can also do an magnetizing curve check to verify whether or not the CT is operating correctly.
RE: Current Transformer
(That max burden is required to be on the nameplate of metering class CT'S per IEEE C57.13 section 6.8.i.1.... the winding resistance is not).
RE: Current Transformer
E.g. 5A CT 6 Ohm burden leads to 150VA with resistance of the secondary winding of about 0.2 Ohms
1A CT with 6 Ohm burden leads to 6VA with resistance of the secondary winding of about 5 Ohms. Hence, the total burden will be 1**2 x (5+6) = 11VA. For mechanical reasons, the 1A CT conductor is not proportionally scalled down for 1A so that its secondary winding resistance may be 1.5 Ohms instead of 5 Ohms.
Reference:
A.R. Van C. Warrington, "Protective Relays Their Theory and Practice," Volume II, John Wiley & Sons, New York, 1978, par. 7.2.1 page 176
RE: Current Transformer
As regards your answer of Dec. 6, my opinion is that CT secondary winding resistance is very low and do normally not exceed 0.1 ohms. Conventional digital polimeters (200 ohms) cannot meassure such a value without serious errors. These are due to resistance of connecting leads from meter to object and to pin contacts as well, which increases the total meassured resistance, in an erratic value amounting some tenths of ohms.
That is why small resistance meassuements requires specific equipments (milliohmmeters) performing four wires.
Julian
RE: Current Transformer
The way I understand things the following should be considered when considering the max load on a CT:
1. the VA rating of the device (the load connected to it)
The impedance does play a role in this calculation by the mfg. Also, the core will play a role amongst others. But for the people using them, I see no reason any other information is necessary as long as the CT is used within the range of currents specified by the mfg. Thanks Buzzp
RE: Current Transformer
Elhouni - out of curiosity... why are you measuring resistance?
RE: Current Transformer
These could include cases where you have to calculate time to saturation of a CT to evaluate whether the relays have enough time to react before the CT output is reduced due to saturation - I agree that this is not your everyday consideration, but we don't really know what Elhouni's application is. Other considerations are given in the references cited above, which show that there are a number of factors that need to be considered when specifying or evaluating CT performance.
By the way, Elhouni, in addition to answering Electricpete's question above, could you advise details of the CT nameplate for our information?
RE: Current Transformer
Good knowledge base ......
To Elhouni,
With all due respect, I think you should state what it is you are attempting to acheive. The data from the CT Manufacturer should be all you need, unless you are trying to incorparate this CT into a bus voltage differential application, where all the CT's must be of matched impedances, otherwise it would be a standard overcurrent application ....
Having said that here is a possible way of figuring out the impedance/resistance of a CT.
Get yourself a current source (power supply, hopefully with a digital display, wired to supply current)
Hook up your CT to the power supply and adjust to a preferred current value i.e. 1 Amp, 5 Amps, etc
Take the voltage reading off the power supply or use a meter.
You now have currrent, voltage ... from this you can calculate the total resistance/impedance ... this will include the power supply internal resistance ...
To get the power supply internal resistance, you get a known resistance (hopefully a 1% resistor), do the same as with the CT. Once you get the total resistance, subtract the known resistance ... you now have the power supply internal resistance.
Substract the power supply internal resistance from the first resistance reading you got from the CT resistance/impedance setup ... you now have the CT resistance
This should do it .....
NOTE - this procedure is valid for both DC and AC therefore resistance/impedance.
RE: Current Transformer
As previously mentioned, for a sensitive dc resistance test you would want to use the four-terminal resistance measurement principle... connect the voltage sensing leads as close as possible to the ct (and ensure they are not carrying the test current). For example if you connected voltage sensing leads to the output of the power supply, you would be measuring resistance of leads plus ct.... if you connect voltage sensing leads direct to the ct you are measuring ct winding resistance with no extra lead resistance. (lead resistance of voltage sensing circuit is insignificant due to low current in the high-impedance voltmeter circuit).
RE: Current Transformer
In this case you would want to take into account the power supply internal resistance since the CT resistance will be as low or lower than the power supply resistance throwing off the final result.
.... this is just a POSSIBLE way of doing CT measurement, it gets you into the ballpark .... there are errors that would need to be considered, as you mentioned lead length, etc ..... but Elhouni is out in the field ... without lab equipment ... if I want the most accurate I would definetely use the 4-wire method you described ....
... another possible way would be to use a DUCTOR ... but it can be a real pain holding down the contact points until you get a stable reading .... and you can only get a DC reading at that ....
.... but these are issues of accuracy that only Elhouni can answer .... how critical is the accuracy? Are ballpark values good enough for his calculations?
as for the the application ... to quote "this value of the secondary winding resistance will be used for the calculations of CT performance against saturation" ... the response by 230842 on Dec, 10 pretty much nailed that one ...
which brings it back to accuracy ..... how accurate does he want his calculation?
... or maybe I am already out in left field .....
RE: Current Transformer
I agree that requirements for accuracy are in the eye of the beholder. My comments on 4-wire measurement were not directed at you.
I'm still at a loss to see the relevance of power supply internal impedance/resistance.
I compute the CT winding dc resistance as V/I where V is measured voltage across its terminals and I is measured current. I don't need to know internal impedance to calculate either of these measured quantities.
RE: Current Transformer
duuuuhhhh .... you are right .... if you have voltage and current .... that is all you need ....
.... I'll just go right back out to left field
RE: Current Transformer
I need to know this value for modeling of CT using the Alternative Transient Program (ATP) to perform some tests like effects of X/R, burden,….etc on CT saturation.
What is given in name plate are, ratio, VA and class e.g. ( 5P20 )
RE: Current Transformer
1. Check the manufacturer's standard CT data sheet for resistance data for the CT
OR
2. Do an accurate bridge measurement of the actual value (see many posts above).
Note that in addition to the nameplate data, you will also need the kneepoint voltage of the CT in order to model the transient behaviour. You will probably have to determine this by test as well.
RE: Current Transformer