Voltage Drop for 2400V system

Voltage Drop for 2400V system

Voltage Drop for 2400V system

(OP)
Dear All,

I am new to this forum and I have one question here. During our design for an airport ILS project, I find I need to calculate the voltage drop for a cable between the step-up and step-down transformer. It's about 3,170ft long and is the load is about 12amp at 2400V. My problem is that NEC Table 9 only provides cable information at 600V. How can I obtain cable info for 2400V?

Your help is highly appreciated and if there is anything wrong with my first post, just let me know.

James

RE: Voltage Drop for 2400V system

An ohm is an ohm and an amp is an amp.  Voltage drop in a function of amp-feet (or amp-meters) through a given impedance.

RE: Voltage Drop for 2400V system

As davidbeach sez, just do the per foot thing.

RE: Voltage Drop for 2400V system

(OP)
Thanks, davidbeach and itsmoked. But can I use the table value for 600V cable to calculate impedance of 2.4kv cable?

RE: Voltage Drop for 2400V system

Cable manufacturer publishes impedance values or charts for MV cables. Contact Okonite, Kerite or Pirelli etc.

RE: Voltage Drop for 2400V system

JCHENNI:

Contact the cable manufacturer and obtain the data from them.

Either:
the approx. impedance / given distance (ohm/km, ohm/mile, etc.)
or
the voltage drop per amp metre (or feet)

Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376

RE: Voltage Drop for 2400V system

Impedance depends on the type of cable (shielded vs. non-shielded) and physical arrangment. I agree with Ralph. The manufacturer should have impedance tables for typical installations.

Is this a series lighting circuit? Airfield systems are commonly series connected circuits, fed by a constant current transformer. In that case voltage drop may not be a significant to the design.

RE: Voltage Drop for 2400V system

The resistance of #2 cu = .194 per 1000 ft and #2 AL = .319
per 1000 ft. An estimate of the voltage drop is

#2Cu .194 x 3.170 x 12 = 7.4 volts  and for
#2al .319 x 3.174 x 12 = 12.1 volts.




RE: Voltage Drop for 2400V system

A rough rule of thumb- One mile per 1 KV.
2.4 KV 2-1/2 miles.
YMMV depending on load.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources