SIZING OF GROUNDING TRANSFORMERS

SIZING OF GROUNDING TRANSFORMERS

SIZING OF GROUNDING TRANSFORMERS

(OP)
I have 2 x 6.6kv, 1MW diesel gensets stepping up through a 2.5MVA 11/6.6kv YnD transformer. The application is standby/peak lopping.
I intend to install an earthing transformer at the 6.6kv terminals of the step-up transformer , and leave the generator neutrals disconnected.
How do I size the earthing transformer ?

RE: SIZING OF GROUNDING TRANSFORMERS

   Generator neutrals are gennerally connected to ground trough a limiting fault current resistor which allows fault detection. Earthing transformer sould take the same fuction and it must whithstand generator side voltage Vg and fault limited current If, so an apparent power:
    sqrt3 x Vg x If.

Julian

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources