FM 200 design concentration

FM 200 design concentration

(OP)
What is the design concentration for Class C in FM-200 system ? saftey factor?

RE: FM 200 design concentration

Are you asking what the design concentration is for a Class C fire? What does the room contain? If its electronics, you also have a Class A fire hazard.

RE: FM 200 design concentration

(OP)
I learned from the internet that class A is used for surface fire and Class C for electrical fires.

for my curiosity to learn more I would like to know the design concentration for Class C fire?

any help is appreciated..

RE: FM 200 design concentration

ASSADEQ,
Is this specified in NFPA 2001 (Clean Agent Fire Extinghishing System)?

RE: FM 200 design concentration

ASSADEQ:

The design concentration is established in its listing. Therefore you need to contact the manufacturer and determine what is required for a Class A fire hazard. See NFPA 2001, section 3-4.2.2. Additionally, NFPA 2001 requires that you provide a safety factor of 1.2.

RE: FM 200 design concentration

(OP)
stookeyfpe:

you are right Class A can be used also for electric applications but this is only if the electrical supply is isolated (shutdown) during suppression.

So, if you have an application where the electrical supply is live you have to consider class C hazard.

thanks for your help

RE: FM 200 design concentration

as posted before yes if the circuit is live you have a class C fire But what is normaly burning is the class A material and you design to that and most of the clean agents carry class C rating also and as stated before each manufacter will have its own requirements for concentration.

http://www.e1.greatlakes.com/wfp/purchasing/jsp/limitations.jsp

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

White Paper: Agile Product Engineering and Improved Product Outcomes
Today’s product development cycle is fraught with difficulties. Increased demands for complex functionality and reduced product development windows cause engineering teams to borrow practices from the IT industry, swapping outdated serial workflows for a more flexible and collaborative design method known as Agile Product Engineering. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close