FM 200 design concentration

FM 200 design concentration

(OP)
What is the design concentration for Class C in FM-200 system ? saftey factor?

RE: FM 200 design concentration

Are you asking what the design concentration is for a Class C fire? What does the room contain? If its electronics, you also have a Class A fire hazard.

RE: FM 200 design concentration

(OP)
I learned from the internet that class A is used for surface fire and Class C for electrical fires.

for my curiosity to learn more I would like to know the design concentration for Class C fire?

any help is appreciated..

RE: FM 200 design concentration

ASSADEQ,
Is this specified in NFPA 2001 (Clean Agent Fire Extinghishing System)?

RE: FM 200 design concentration

ASSADEQ:

The design concentration is established in its listing. Therefore you need to contact the manufacturer and determine what is required for a Class A fire hazard. See NFPA 2001, section 3-4.2.2. Additionally, NFPA 2001 requires that you provide a safety factor of 1.2.

RE: FM 200 design concentration

(OP)
stookeyfpe:

you are right Class A can be used also for electric applications but this is only if the electrical supply is isolated (shutdown) during suppression.

So, if you have an application where the electrical supply is live you have to consider class C hazard.

thanks for your help

RE: FM 200 design concentration

as posted before yes if the circuit is live you have a class C fire But what is normaly burning is the class A material and you design to that and most of the clean agents carry class C rating also and as stated before each manufacter will have its own requirements for concentration.

http://www.e1.greatlakes.com/wfp/purchasing/jsp/limitations.jsp

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Related News

Resources

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close