Metric Conversions
Metric Conversions
Hey all
I seem to be having some problems converting Imperical units to metric as i am a uk engineer. The problem is to do with Shear in a flat slab.
Allowable Vc=4*sqrt(Fc)*bo*dv
Imperical Units
Vn=102,000lb
fc=4000psi
bo=83in
And the imperical depth for the slab is given as 4.86in
Mertic units
Vn=451kN Conversion factor = 4.448222
fc= 27.576Pa Conversion factor = 6.894757e-3
bo=2108mm Conversion factor = 25.4
Yet my depth is coming out at 10.18mm
I can't seem to figure out the problem
Any help would be much appreciated.
Many thanks in advance
Imperical Units
Vn=102,000lb
fc=4000psi
bo=83in
Mertic units
RE: Metric Conversions
Try Vc = 3.3 EE-4 sqrt(Fc)*bo*dv
dv = Vc/[3.3 EE-4 sqrt(Fc)*bo] in mm
where Vc = 451 KN
fc = 27.576 MPa (your conversion factor was for psi to MPa)
bo = 2108 mm
Bring back the HP-15
www.hp15c.org
I don't think 4*sqrt(Fc)*bo*dv equals pounds?
lb^0.5 * in * in lb^0.5 * in * in
(in^2)^0.5 in
= lb^0.5 * in ????????????????
We must not forgert that many of these equations are empirically derived based on research data and mathematical modelling to test validity of data. Often several contants (Davybeano's case the number 4) come into play. Use of and MLT (mass, length, time) units appraoch to check validity thus may not always work.
I think that equation is set up to use f'c in units of psi only. (You'll always have to convert your final answers to metric and use f'c in psi).
The 4 has to be converted also by dividing by the sqrt of the conversion factor = sqrt(144.----) = 12
so
4*sqrt(Fc)*bo*dv
with Fc in psi
becomes
4/12*sqrt(Fc)*bo*dv
with Fc N/mm2
Vc = 0.333*sqrt(fc)*bo*d with fc in MPa, bo and d in mm gives Vc in N similar to what I posted earlier when solving for Vc in KN.
Another easy method of verifying equation
If you do not have the metric version of ACI 318, just look at equation 11-3 in the 1997 UBC Sec 1911.3.1.1/ACI 318-05 Sec 11.3.1.1...compare the imperial and SI versions of the equation...substitute fc for f'c, bo for bw and dv for d. Now the imperial version looks similar to Davybeano's except the constant is 2 instead of 4....while in the SI version, the constant is 0.166.
Therefore if the constant in the imperial version were doubled to 2*2 = 4 (Davybeano's eq was Vc=4*sqrt(Fc)*bo*dv) , it follows the constant in the SI version would also have to be doubled to 2*0.166 = 0.332
Finally plug Davybeano's numbers in the imperial version of the equation he provided...then try it with the metric version indicated in first paragraph. Do it again with a different fc (say 6,000 psi/41.4MPa)and repeat with both imperial and SI equations. It'll check out.
This may be the issue.
I would do the whole calc in imperial, then convert your result to metric, not trying to convert all terms in these empirical equations.
tg
_____________________________________
I have been called "A storehouse of worthless information" many times.
http://www.onlineconversion.com/
Very useful.
Jeff
Jeffrey T. Donville, PE
TTL Associates, Inc.
www.ttlassoc.com
ALL UNITS ARE COMPARISONS AND ARE THEMSELVES DIMENSIONLESS.
Merry Christmas