initial fault & Ultimate fault

initial fault & Ultimate fault

initial fault & Ultimate fault

(OP)
I got some data from some utility company, they provided 'inititial fault & ultimate fault data',
I am not sure what they exactly mean? Are they minimum fault and maximum fault?

RE: initial fault & Ultimate fault

My (guess) the original response (exponential) followed by the steady state fault.

RE: initial fault & Ultimate fault

You should ask for clarification, but sometimes utility will provide actual fault data for the present system, but also give you a larger value indicating what the fault duty could be in the future, based on system expansion and growth.  

RE: initial fault & Ultimate fault

Fault provided by the utility as presently constructed and fault provided by the utility after some future work (which may or may not occur)??

RE: initial fault & Ultimate fault

(OP)
I was told by my superviser that initial  fault was Min. Fault Data, Ultimate fault fault is Max. Fault Data. But I doubt that.

RE: initial fault & Ultimate fault

Initial: Fault current available today.
Final: Fault current available when they install the largest transformer upstream to serve your service.

RE: initial fault & Ultimate fault

Dear SELEC,

From my knowledge with my national utility company, when we asked for fault values, they will give the MINIMUM fault (say 4000 MVA and translated into kA @ 132 kV) and MAXIMUM fault (say 5600 MVA) values.

The maximum is what the utility has predicted now and some future forecast. They also need this for their own system protection planning eg. to consider for new equipment and planning for system expansion. And this value might change if the predicted generation/loads are confirmed.

The minimum is fault generated when minimum generation is connected to grid eg. during island operation of some of its power plants.

Not very sure of what your utility means but again, no harm in asking them. They could use a different software and the terms used be different?

My 1-cent opinion

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources