Why limit on light gauge backed masonry veneer height?

Why limit on light gauge backed masonry veneer height?

Why limit on light gauge backed masonry veneer height?

(OP)
In ACI 530 table 6.2.2.3.1 there are height limits for clay masonry veneer backed by light gauge framing.  The commentary does not explain what drives these limits.  Thermal and moisture expansion of course have to be considered in the design and detailing of the veneer but I wondered what if any other factors drove this requirement.

RE: Why limit on light gauge backed masonry veneer height?

Generally speaking, if a clay masonry veneer is relatively much stiffer than the steel studs behind it, the clay masonry veneer will try to resist wind or seismic load without transferring the load to the studs (load always takes the stiffest path).  With flexible studs, the clay masonry veneer will take lateral load until it fails, at which time it will crack horizontally and begin transferring the lateral load to the studs.

Stiffening studs is an attempt to prevent cracking of the veneer.

I am more liberal than most engineers, in that I generally allow L/360 deflection of wood or steel studs behind clay masonry veneer.  Many engineers limit deflection to L/600.  I once heard a speaker say that no mattter how stiff you make the studs, they are still not stiff enough.

DaveAtkins

RE: Why limit on light gauge backed masonry veneer height?

(OP)
David thank you for your answer.  However I think something else is driving this code requirement.  The chart I cited limits the height above the foundation for which the veneer can be self-supporting to 30'.  The back-up walls need to be stiff enough, no doubt, but I believe that is a separate issue.

Am looking at a facade design for a 4 story building with a floor-to-floor height of 11 feet.   The light gauge stud walls will be designed to carry vertical floor loads and also limit lateral deflection to L/600+- under wind/seismic.  But, because of the code requirement cited previously, I will also need to vertically support the veneer at at least one of the intermediate floor levels.  Will have a soft hor joint at the support level(s).  The architect is going to ask why the code requires this and I don't have a good answer (yet!).

Also, in ACI 530 sec 6.2.2.3.1.3, "the weight of the veneer shall be supported by noncumbustible construction for each story above the height limit given in table 6.2.2.3.1."  So it sounds to me like the vertical support has to be provided at EACH floor level above the 30' limit.  Theres an obvious cost here and I wonder what is driving this requirement.

Any additional comments appreciated.

RE: Why limit on light gauge backed masonry veneer height?

It may be a more empirical judgement thing on the part of the code writers.  Having more than 30 feet, all supported below, could be considered a dangerous condition in that an impact or other distress below might cause a huge amount of brick to fall.

RE: Why limit on light gauge backed masonry veneer height?

These limits have to do with the vertical growth of the clay masonry relative to the structural frame. If I recall correctly, the estimated growth is about an 1/8" per 10 feet of height. When used in combination with a concrete frame, the differential between the growth of the brick and the shortening of a concrete frame due to shrinkage and creep can be quite dramatic.

If shelf angles are not used on taller buildings, it can cause failure of sealants, cracking of brick, drywall, windows, etc.

See

http://www.looksmarthomeimprovement.com/p/articles/mi_m0NTA/is_5_16/ai_101943896

for more information.





RE: Why limit on light gauge backed masonry veneer height?

here is a link to Valley Block and Brick website.  at the bottom of the site is a link to NCMA TEK notes.  There are guidelines for masonry veneers, including control joint requirements.  http://www.valleyblockandbrick.com/  Perhaps the NCMA TEK notes will provide additional information to help you.  doesn't necessarily answer your question, but I agree with JAE about emperical issue and with Dave about the stiffness of the studs.  Over the last 10 years, I've designed several buildings with metal studs backing up brick veneer using the L/600 deflection criteria and so far have had no problems.  obviously, the taller the wall and studs, the more lateral deflection will govern the stud size to maintain the L/600.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources