Is a disconnect after harmonic filter required?

Is a disconnect after harmonic filter required?

Is a disconnect after harmonic filter required?

(OP)
I am working on a electrical chiller replacement job.  It involves replacing an constant speed chiller with a VFD chiller.  I planned on using the existing CB to feed a new harmonic filter physically inplace of the old motor starter(adjacent to existing powerpanel) and then connecting the filter to the unit mounted VFD w/CB.

An engineer says this is a violation of the NEC 25 FT Tap rule because the cables are 30 FT and a disconnect is required after the filter.  

The filter consists of a two series reactors with a capacitor bank tapped after the first reactor.  There is no electrical isolation, like a transformer.  I am considering this filter integral to the dedicated branch circuit and not a tap rule application, therefore, no disconnect is required.

All the cabling is sized for full load.  Which view correct???  Help is greatly appreciated.

RE: Is a disconnect after harmonic filter required?

I would say your view is correct. I have run into electrical inspector requiring a local (within sight) disconnect on "line" side of a reactor, citing safety for maintenance, but not on the secondary side.

It is not a seperately derived source so secondary side disconnect is not required, as it would be in case of a transformer.

RE: Is a disconnect after harmonic filter required?

(OP)
Thank you for the response rbulsara.

RE: Is a disconnect after harmonic filter required?

Quote:

It is not a seperately derived source so secondary side disconnect is not required, as it would be in case of a transformer.
Transformers are not required to have a means of disconenct at the secondary.  The may be required to have secondary overcurrent protection, but that can be located anywhere.  The secondary conductors, will however, in most cases, require overcurrent protection at or near the transformer.
Don

RE: Is a disconnect after harmonic filter required?

resqcap:

You are correct in interpretation of the Code.

I figured that was the intent of "other" engineer that OP referred to,as a tap rule was mentioned. Conductors need to be protected at the origin and a separately derived source (tranformer) would be a new origin but not a reactor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources