Motor inrush current

Motor inrush current

Motor inrush current

(OP)
Hi, Fellows,

I am having trouble with Commissining.Whenever we started a motor (very small 25HP) it always tripped our main breaker, instead of branch breaker. From TCC curve, Main(SR750) shouldn't trip while motor starting. What is pazzling us that what could be the source of inrush current beside motor starting and energzing transformer in a compressor station. Is it possible that branch breaker refused to operate for some reason?

RE: Motor inrush current

We need more info expecially abou your circuit
Is the motor connected directly yo the breaker or there is a transformer after the main breaker?
Is the main breaker delay correctly setted? Moto can have a starting current of 6 or more times the rated current

Try to be more detailed

RE: Motor inrush current

(OP)
the motor is not directly connected to the branch breaker.The max FLA is 800A, plus motor inrush, Max Current the main bus will draw is only 1100A. The coresponding time for Main( SR750) is ~60s, which is long enough to avoid trip the branch circuit. I am assuming there maybe some other source of inrush current.

There is only one LTG Transformer(30KVA)in parallel with motor feeder.

RE: Motor inrush current

Does the main have a ground trip?  It may be set too low and is responding to false residual during the motor start.

RE: Motor inrush current

(OP)
Yes, the main has a residual ground trip, which is set same as phase current setting with a diffrent curve.Is the false residual value very high during motor starting?

RE: Motor inrush current

The false residual is caused by saturation of the CTs.  Somehow though, it seems that a 25HP motor shouldn't be causing that much inrush.

Sounds like time for good recording meter to gather voltage and currents while the motor is starting and the breaker is tripping.

RE: Motor inrush current

Inrush current on a motor is different than starting current, although many people mix up the two terms. Inrush is a short duration spike that occurs when magnetizing the stator windings, and can be as high as 20 times the motor FLA depending on the motor design. It only lasts for a maximum of 2 cycles however. If your trip curve on the feeder relay does not take that into account, it may cause a trip.

Starting current is 500 - 800% of motor FLA depending on the motor design, and can last several seconds or longer depending on load. Again, if your feeder relay does not take that into account, it will trip as well. The settings you described sound like the long time I2t settings for thermal current.

Eng-Tips: Help for your job, not for your homework  Read FAQ731-376

RE: Motor inrush current

I agree both with davidbeach and jraef.
The problem can be one of hte two mentioned
I can be the saturation of the CTs or also the not so good precision of them which cause a false ground current alarm.
Bu als can be the magnetizing current flowing in the motor at the moment you are closing the breaker.

Does the breacker open immediately or after some seconds?

I think the best action is going on the field and record the current waveforms.

RE: Motor inrush current

Does this happen when a particulalr motor is started or any motor?

Size of main? Voltage? is there intervening trasnformer between the main and the motor?

I dont think you posted enuff information...

RE: Motor inrush current

(OP)
Hi, Fellows,

Thank you for the feedbacks. I already solved this puzzle.
i phoned th site and they told me they were trying to satrt three 25HP Motors simutaneously, causing a huge asymetrical inrush current which tripped Main.

I suggested them to inrease the IOC od SR750 connected to Main. Hopefuly that will solve the problem.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources