I have a problem,    
 
I've been trying to configure the card CM900 to  PLC modicon Compact 984, I don't  understand the way I can download the file DL.DAT toward the PLC.    
    
Could somebody  tell me how to do it?

Thank's in advanced.
    

RE: How can I setup the CM900 to modicon 984?

Here's the help file from the CM900 loadable disk....


**** CM900 Program Diskette ****
Standard Program Version
1.0E

This Diskette contains several files related to the CM900.
Included is the Standard Program, terminal-emulation/utility
program, and the CM900 personality. Following is a list of the
files on this diskette with a brief description of each one.
Please refer to the CM900 Operator's Manual and the SP1011 Software
Manual for additional information on the use of these files.

CM900ST.HEX - Compiled Standard Program
DL.DAT - CM900 personality, Needs to be loaded on the Host PLC,
         does not appear in PLC logic
EC.EXE - terminal-emulation/utility program for downloading compiled software


*** Instructions for updating the CM900 Standard Program

1.  Type EC[cr]
2.  Press [ctrl][A] to enter download mode on the CM900
3.  It will prompt with:
    CM900 Compact 984 Interface Module V1.0A
    (c) Datalogic 1993, All rights reserved

    Press [CTRL][D] to enter monitor... hit
4.  Press [ctrl][D] to enter download mode
5.  Press [cr].  The CM900 should respond with a hyphen '-'.
6.  Press [PgDn] to download new program
7.  It will prompt with *.hex, asking for proper extention
    to download - this is correct press [enter]
8.  It will then transfer the prompt to the lower section of
    the screen and request that you hi-light the file to download
    and press [enter]
9.  EC will initialize the port and the proceed to download
    the program. (address will appear on the screen while it is
    downloading)
10. When the CM900 is done downloading it will then attempt to
    enter run mode.  
11. If running the standard Datalogic program it will prompt:
    CM900 Standard Program verison xxx
    This program requires the loadable FN01.DAT to reside
        within the PLC for passing data between the PLC and CM900

    Press [CTRL][D] withing two seconds to enable Debug mode...
    Starting Program ...... Without Debug mode enabled

www.krkautomation.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources