Analysis for Steel Plate
I have a 3/8" plate that is span over a 26'x6' area and is supported every 4'3".  The circumference is welded.  I have a uniform load for the area at 2,200 lbs/ft or a 515 lbs/ft^2 and I also have a point load that is 4,985 lbs (there are two of them at 3' apart)
How do I go about analysis a plate for moment shear and deflection?
The formulas would really help and how the K or C factors are found.
RE: Analysis for Steel Plate
Try 'moments & reactions for rectangular plates' by W T Moody, A Water Resources Technical publication - Engineering Monograph 27 (my copy is dated 1970 so it may be out of print).
This gives 5 different edge conditions with 10 different combinations of loads.
Edge conditions such as 3 edges fixed & one free, 4 edges fixed etc etc.
Loading charts include uniform loading for 1/3, 2/3 & full depth, water loading 1/3, 2/3 & full depth, etc.
Derivation is included but the charts give all the info req'd.
Charts are given for a/b from 1/8 to 3/2 (a is semi width & b is depth).  Cantilever moments & beam moments are given for each 20% of height & width, as well as reactions.
This monograph was produced by the USBR & may still be available from them.  Check with their office (Denver Colo) or with the Superintendent of Documents, Gov't Printing Office, Washington DC (at least it was in 1970).
I have verified sections (with other methods) when I was involved with designing 10m deep conterfort retaining walls for a dam spillway.
BarryEng
Call NTIS at 1-800-553-6847.  I called and they have it.  The ordering number is PB96172242.  $42.50 + $5.00 s/h.
www.ntis.gov