Capacitor Plage - Premature Electrolytic Capacitor Failure
Over the past several years, our industrial facility has experienced many electronics failures where the root cause has been capacitor failure due to electrolyte dry-out. The problem has been seen in power supplies for PLC's, protective relays, and process control equipment installed in the later 1990's.
I began investigating a recent incident, and suddenly remembered all the issues around motherboards and computer power supplies a few years ago. Our equipment is the same age as the failed computer equipment. I found an interesting wikipedia article that mentioned an IEEE Spectrum article from February 2003, titled "Bad Capacitors Mucking Up Motherboards".
This article only dealt with the personal computer side if the issue.
The goal of this posting (which will be cross posted into relevant forums) is to determine the extent of industrial failures and to estimate an approximate window of when the bad equipment was installed. This is due to the relative silence from the capacitor and equipment manufacturers on the issue.
The questions are as follows:
1. Has your facility experienced multiple failures with the root cause being bad capacitors causing voltage instability?
2. If yes to #1, what year was the device manufactured?
3. If yes to #1, what as the manufacturer (if it is appropriate to tell) or what was the equipment type.
Please also share any further information you may have on the subject. We are looking to determine the extent of this phenomena and our exposure to future events; one event can cost our industry several M$'s. Thanks in advance for any information.
RE: Capacitor Plage - Premature Electrolytic Capacitor Failure
I have had no more than perhaps ten cases of bad electrolythic capacitors over the three+ decades that I have been exposed to equipment failure in paper mills, steel works, power plants, workshops and offices.
The ones I remember are:
One Measuring machine of Swiss origin. The capacitor was a Philips type and the age was well over twenty years. The ripple current had heated it to the extent that the wire insulation had turned brown/black. Natural aging, I would say.
One press with linear scales and automatic positioning. Capacitor in PSU gone bad. Also natural aging.
One old PLC (Elektronlund) with bad capacitor. Natural aging again.
Eleven HP laser printers where the capacitors exploded after very short time. Reason here was severe notching of mains voltage due to heavy (800 kW) thyristor controlled heater on distribution transformer secondary. Mistake by the electricity company. The transformer was supposed to supply the industrial load only, but did double duty supplying a research office.
I cannot recall any capacitors that were bad quality. There is some concern with DC link capacitors in PWM frequency inverters. But I have yet to find one that really causes problem. The oldest inverters I get in touch with are ABB YRRA and Siemens Simovert P from the eighties.
This will be a very interesting thread, I urge all and everyone that has experienced electrolythic capacitor failures to write about it here.
Gunnar Englund
www.gke.org
Many years ago, I remember mains filter capacitors in vacuum tube tv sets exploding. Well the ends blew off with a bang... caused by age in waxed paper capacitors.
(Remember them? Horrible waxy yellow things, always sticky).
I have directed that future posts in the other forums be directed here.
The interesting wikipedia link is here:
http://en.wikipedia.org/wiki/Capacitor_Plague
If you have a subscription, the IEEE Spectrum paper is rerferenced in the original post.
Of course, this is all from memory...
Dan
Owner
http://www.Hi-TecDesigns.com
Right now, I know one protective relay manufacturer, of whose we have very many, and the consequences of false tripping are high. The costs associated with repair/replacement are high and a better understanding of failure probability would help make the case for corrective action.
I think that my lack of bad experiences with capacitors comes from the fact that I am not asked to find what's wrong with consumer products. I wonder why my radios, TV sets and other consumer products also behave relatively well? I remember having just one bad capacitor in the power supply back in the seventies. The TV set was so old that it had electron tubes in it.
Gunnar Englund
www.gke.org
I believe some of the larger industrial electronics manufacturers have outsourced some of the subassemby for their devices with cost as the primary factor. The units come in and pass Q/A testing, but rapidly fail when placed into service.
I found a couple more interesting links.
http://www.niccomp.com/taiwanlowesr.htm
h
There are several websites dedicated to motherboard failures on this issue.
The other text I've found said it's only the high water content (40% - 70%) aquious electrolyte aluminum capacitors that are failing. The other two aquious types are Dipropyl Ketone and Ethylene Glycol with less than 25% water content.
Not suprisingly, the higher water content units are cheaper. I suspect these units are being substituted to save costs while meeting specification.
The 105 deg C versions are allegedly better.
I have no idea what the minimum form time/curve per volt/farad would be to have some meaningful value. It would probably be to long for a consumer item.
Barry1961