Purging fuel lines.
4

Purging fuel lines.

Purging fuel lines.

(OP)
Our site requires that we purge fuel lines (natural gas and butane) prior to any maintenance. We do this with N2 at the present time. We have a fairly good supply of CO2 on site. Is there a downside to purging fuel lines with CO2?

RE: Purging fuel lines.

You need to check the gas properties of each and determine displacement volumes and rates, etc...the only displacement using CO2 that I'm familiar is using CO2 inbetween air and hydrogen gas/degas operations in hydrogen gas cooled generators.  The CO2 is never left as a blanket...

Whe laying up a power piping system it has always been a nitrogen blanket as this is inert...retards corrosion.

RE: Purging fuel lines.

CO2 is too heavy, if not done carefully: you may have CO2 sitting at the bottom of the pipe and natural gas sitting on top of it...
the only way to ensure that there are no gas pockets is to use a large amount of CO2 and sample ALL the high point vents to ensure that the CO2 concentration is higher than 97% in volume.
similar to the example cited by turboco1.

also, CO2 is much more expensive than N2... the main reason to use N2.

saludos.
a.

RE: Purging fuel lines.

Carbon dioxide - Solid particles of carbon dioxide become charged during discharge from the nozzle and can lead to incendive sparks in a flammable atmosphere [3, 5].

That is from --Static Electric Discharge Hazard On Bulk Oil Tank Vessels


International Safety Guide for Oil Tankers and Terminals (ISGOTT), advises against it but I don't have the manual here to quote from it.

More investigation is recomended before you do it



RE: Purging fuel lines.

In the water industry they use CO2 to lower pH by injecting it in the water. If water is present in the fuel line could it form an acid? Carbonic?? CO2+H2O

RE: Purging fuel lines.

(OP)
Great stuff everyone! Many thanks!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources