Transmission line conductor current rating vis-a-vis the wind velocity
Transmission line conductor current rating vis-a-vis the wind velocity
(OP)
Current rating of a OHL conductor is a function of allowable temperature rise and the wind velocity for a given location.
Many specifications indicate what should be the refenerce ambient temperature for current rating calculations and the maximum operating temperature rise is generally limited to 85degC (AAC/ACSR conductor).
How about the wind velocity, is considering 0.5m/sec more common or should I consider Still air conditions (om/sec) that happens to be the worst condition from the point of convection heat loss?
Any suggestions!!
Thanks in anticipation.
Many specifications indicate what should be the refenerce ambient temperature for current rating calculations and the maximum operating temperature rise is generally limited to 85degC (AAC/ACSR conductor).
How about the wind velocity, is considering 0.5m/sec more common or should I consider Still air conditions (om/sec) that happens to be the worst condition from the point of convection heat loss?
Any suggestions!!
Thanks in anticipation.






RE: Transmission line conductor current rating vis-a-vis the wind velocity
If you have no control over operations, or are designing for worst case, it would seem appropriate to design for still air.
RE: Transmission line conductor current rating vis-a-vis the wind velocity
One viable alternative is using the dynamic rating techniques sometimes called "real-time rating". Weather stations or other mean of monitoring and predict weather and sag along the line corridor is required to re-evaluate the line capability at any specific time.
A few options of dynamic rating systems are described in the following links
http://
ht
RE: Transmission line conductor current rating vis-a-vis the wind velocity
For planning purposes these are OK but in actual operations I'd suggest a more conservative approach depending on age and condition of the line, conductor, hardware (splices clamps etc.) since these are the first to fail due to thermal runaway.
RE: Transmission line conductor current rating vis-a-vis the wind velocity
The 2 feet per second speed is often considered a minimum generated by natural convection around the conductor due to the temperature difference between the conductor and the surrounding air. Larger wind speeds should be used with caution, even if you are monitoring local conditions for "real time" rating.
RE: Transmission line conductor current rating vis-a-vis the wind velocity
Looking at the equations in IEEE 738 and using Drake conductor, I got that the crossover between natural and forced convection was more on the order of 0.4 ft/s, but would of course depend on the temperature differential.
RE: Transmission line conductor current rating vis-a-vis the wind velocity
RE: Transmission line conductor current rating vis-a-vis the wind velocity
Is there no codal guideline as to the minimum wind speed to be considered, say perpendicular to the conductor!!
Thanks in anticipation.
RE: Transmission line conductor current rating vis-a-vis the wind velocity
_____________________________________
I have been called "A storehouse of worthless information" many times.
RE: Transmission line conductor current rating vis-a-vis the wind velocity
Free convection air current is taken as 0.2-0.5ft/sec. All formulae for Convectively dissipated Watts are applicable only above "these" air current values (- look for specific formula for application). Standstill air cannot dissipate convective heat, by logic! Your Wc will be zero, if you use air current of zero m/sec!!; standstill air can still be achieved in lab conditions though.
Average wind velocity of a location or the region is normally available in the GENERAL DESIGN CONDITIONS of any specification; a good one will have min and max values. While the 'max' value is used for calculating Wind Loading of structures, the 'min' value is used for Heat Dissipation calculations!
Codal requirements can be looked into if you could tell whether it is for IEC or for ANSI/IEEE world.
Best regards,
RE: Transmission line conductor current rating vis-a-vis the wind velocity
One particular Client's specification calls for the use of 0.609m/sec!
Let us know what was finally accepted in your case.
best regards,