i am having hard time designing for fire protection improvement for normal open doors..i am looking for devices which will not allow entry to the where fire or smoke was detected but occupants can exit and can function either way..it is a two door swinging type..PLEASE HELP.....





RE: fire protection improvement
1) Are these doors in an egress path?
2) Are these doors penetrating a fire barrier or fire wall? If so, what is the fire resistance rating?
3) Is the building protected by automatic sprinklers?
4) Is the building in the U.S.?
I've never seen a fire rated door assembly as you have described. The fundamental question is once folks have exited from a compartment or area that is involved in fire, why would want them to re-enter this area?
Please post more information
RE: fire protection improvement
RE: fire protection improvement
RE: fire protection improvement
I'm doing a translation into English, the document is Technical Specifications for a Fire Protection System of a high-rise building. I cannot find the proper name for the waterpipe that's used for fire-fighting purposes. Is it fire watermain? Fire waterline?.. (Not the little sprinklers and stuff.. the whole kit'n'caboodle system). Many thanks :)
RE: fire protection improvement
standpipe system
and there is class I, class II and class III designations, they are covered by national fire protection assoc standard # 14.