Single-phase Delta to Wye transformer connection

Single-phase Delta to Wye transformer connection

Single-phase Delta to Wye transformer connection

(OP)
This may be a silly question, but I could do with confirmation.  I have a 2400V delta 3-phase distrbution system that is being converted to 4160Y.  There is a two bushing single-phase transformer 2400 delta primary to 120/240 secondary.  This transformer should work being connected line-to-nuetral on the 4160Y/2400V system?  One of the primary bushings is being reconnected from line to nuetral as part of the conversion.  The reason I ask is that all of the other transformers are marked 4160/2400 on the nameplate and this one is just 2400 delta.

RE: Single-phase Delta to Wye transformer connection

Connected line to neutral on a solidly grounded system, the transformer will only see 2400V and should work just fine.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources