Emergency Power Generator damaging Electronic Ballasts ?

Emergency Power Generator damaging Electronic Ballasts ?

Emergency Power Generator damaging Electronic Ballasts ?

(OP)
At my facility I have roof top substations and which some of them I have emergency back up nat gas generators.  The generators provide power to 277 Volt Metal Halide Lighting for the production floor and also 277 v flourescent T8 lights with electronic ballasts in the rooftop substation itself.    When recently testing the generator and transfer switch per NFPA requirements,  I noticed that after the generator was running for 10+ minutes the flourescent lights started oscilating in light output the more and more the generator was left on.   50% of the lights ended up dying,  since then I found out the bulbs and fuses are still good but the electronic ballasts are evidently fried.   I am thinking of testing it again and perhaps putting a Fluke Power Quality analyzer on the generator output to see what is going on.  The analog meter on the generator and a Fluke digital meter showed a solid 277 volts output while the generator was running.     Does anyone have any suggestions as to what is going on here ?

RE: Emergency Power Generator damaging Electronic Ballasts ?

Did you happen to check the frequency output of the generator?

RE: Emergency Power Generator damaging Electronic Ballasts ?

Check your harmonics....

what loads are running at site ?

rugged

RE: Emergency Power Generator damaging Electronic Ballasts ?

May be you should have a close look at the generator AVR and see that the same is in Auto.

It will help if you can keep voltage little lower (should pose no problem provided the load is mostly lighting).

How about harmonic filters in the system, are they available / working (electronic filtesr introduce harmonics in power supplies that can cause difficulties especially when the system is not connected to the grid).

RE: Emergency Power Generator damaging Electronic Ballasts ?

What is your load power factor?  With older equipment, I have seen some voltage regulators start pumping with switching regulator loads.  The switchers vary their power factor as they regulate and the voltage regulator O/p varies and the switches changes power factor again in a vicious cycle.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources