Im working on an efficiency project and seek to gain some information to assist me with this. Hope that you can throw me some pointers for this.

Air flow temperature drop - If the air coming into an AHU is more than that leaving an AHU then there has been some temperature absorbed - how could this be worked into a watt figure - is this possible ? I know I need to get a l/s figure for the AHU and an adjustment figure for the pressure drop created by the filter media. But would this be a viable way to take this forward ?

Rugged

RE: Power Absorbed

Just ignore all and use Q = 1.08 x cfm x dT, dT in deg.F. This give the heat in btus.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources