Cable Size

Cable Size

Cable Size

(OP)
Hi Everyone,

I have a 2000 kVA transformer 27.6 kV/ 600 V
The transformer and electrical service cabinet both are going to be outside and located very close by each other.
The code asks for breaker and conductor (secondary) not more than 125% of rated current.
1)What would be the most economical secondary cable.(2500 amps considering the 125%)
2)Is there any specific rule regarding not having splitter box for that level of amps? (as oppose to have a real nice distribution panel)

Thanks in advance

 

RE: Cable Size

My opinion:

Use 500kcmil conductors (380A).  Anything over that and a contractor will want to strangle you.  I'm not sure what you mean by a "splitter box".

Mike

RE: Cable Size

(OP)
By splitter box I mean:

The outgoing cable after main breaker would go to a set of terminals which all of feeders to branch breakers are tied to those terminals.

As oppose to have a real bus bar and feed the branch circuit breaker from bus bar.

For 500kcmil I should use 7 conductor per phase (wow)




 


RE: Cable Size

Please correct me if I am wrong as I am still fairly new to this myself.

I am using the Ontario Electrical Code (OEC) as a reference here so you may have to look into the requirements in your area.

In the OEC it states that if you use single copper conductor in free air you can push 660 A down a 500MCM cable, so with this being said if you can get the required spacing between cables you should be able to use less then 7 per phase.

RE: Cable Size

Well..

In NEC land, I don't believe there is any Code section restricting you from doing what you're explaining (assuming I'm understanding you correctly).  However, I don't know that what you're proposing is a good idea.  I hope you reconsider your position, and use a service entrance rated switchboard.

Mike

RE: Cable Size

I would look at bus duct.  With that type of load and a very short run, the lenght differences in the parallel runs can become a problem.
Don

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources