Weld Length and Pitch
I have a fillet weld that specifies a length(.38") and pitch(1.00"). I need to know the tolerance of the length and pitch, I've looked in both AWS A2.4 and A3.0 with no avail. Could someone point me in the direction of the spec that defines this?
Nathan
Nathan
RE: Weld Length and Pitch
AWS D1.1 states that the minimum length of the fillet weld is four times its leg size. Stated another way, the maximum size of the fillet weld is one quarter of the weld length. The weld start and crater is included in the length, provided the crater is filled to the full cross section.
Nathan
Weld size - size specified is the minumum leg size permitted
Weld length - the minimum length of each weld segment permitted
Unwelded spaces - pitch minus length = the maximum unwelded space between weld segments
With that in mind, in the absence of a workmanship standard, a continuous weld that has the proper size (leg dimension) would be acceptable even if the intermittent weld was specified as 4 inch (length) on 10 inch (pitch). The workmanship standard would be a requirement imposed by the customer or the fabricator could have their own "in-house" standard. The welding symbol, in itself, does not imply any standard tolerance, other than specifying minimum length and size. Even those minimum can be played with by the governing standard. For instance, AWS D1.1 Structural Welding Code/Steel allows the fillet weld to be undersized by as much as 1/16 inch provided it does not exceed 10% of the weld's length (paraphrased).
Hope this helps.
Al