An interesting problem has occured on some recently installed PV installations. On the most project there are 4-240 volt single phase grid-tied inverters connected to a 240V/3P/4W Delta electrical system. L1 & L2 of inverter 1 or I1 are connected across phases A-B respectively, I2 across C(L1)-A(L2), I3 across B(L1)-C(L2)and I4 across C(L2)-A(L1). The neutral is tapped on the utility transformer at the center of A-C. When connected like this, inverter 1 and only inverter 1 will not connect to the grid(this means any inverter in position 1 has the same failure), the failure shows up as a XFMR Disturbance, meaning a utility transformer problem. But, if the line leads for are reversed, meaning phase A to L2, B to L1. The inverter starts right up every time. This same problem occurs only and on every 240V/3P/4W Delta project. I believe the problem is something inherent to the Delta system itself and not the cause of system loads, but I need some help explaining why this works.   

RE: Grid Tied Inverter On 4 Wire Delta System

RU sure you are not connecting from A to the center tap.  Gottal watch out for wild leg connections.

RE: Grid Tied Inverter On 4 Wire Delta System

(OP)
There is no neutral at the inverter, connections are as previously explained.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources