Hollowcore roof diaphragm
I am working on a structure that has load bearing masonry walls with a hollowcore roof.  Where can I find the diaphragm capacity of an 8" hollowcore with 2" topping and reinforcing? Or is it as simple as finding my chord force and designing reinforcing such as in a beam?
RE: Hollowcore roof diaphragm
Contact your local hollowcore supplier. They should have the test data that you are looking for.
Spancrete is one of our local suppliers in this area and I know they have datasheets with this info. and their engineers can also walk you thru the procedure.
Try the following book.  You'll want chapter 4.
MNL-126-98
PCI Manual for the Design of Hollow Core Slabs
http://www.pci.org
I use the book that UcfSE mentioned.  The PCI design handbook also might be useful.
You can analyze it as a deep beam to get your chord forces.  The keyways, along with the topping reinforcing will resist the shear.
UcfSE's reference, and the PCI manual is a good one.  If you don't have it re-post and I'll try to guide you through the procedure.