(OP)
24-0" x 60'-0" high ss tank with bottom conical is to be provided cooling jacket on outside of shell and bottom cone. Inside pressure in the jacket would be 56psi @ -4C.Inside pressure in tank is very low and will be designed per API 650.From your experience, could you please review and recommend type of jacket that  would be more efficient and economical to fabricate and install.

Thanks in advance for help.
 
                                                                                                                            

RE: Cooling jacket for 22"-0" Fermenting tank with bottom cone

If this is process cooling then I don't think external coils will be effective on such a large dia tank. You may want to consider internal plate coils such as those supplied by Tranter.

http://us.tranterphe.com/phe/platecoil/platecoil.htm

RE: Cooling jacket for 22"-0" Fermenting tank with bottom cone

Dimple plate has been used in the past

RE: Cooling jacket for 22"-0" Fermenting tank with bottom cone

pve,

I agree with the comments made by "codeeng"... The aspect ratio (24:60)of your tank is not suitable for exterior cooling systems. There would be a tendency to develop thermal stratification in the liquid.

Instead, consider an external pumped system with an external heat exchanger and, possibly, additional liquid return nozzles on your tank. There are maintenance and layout advatages with such a system. The heat exchanger, valves etc can be isolated and maintained much easier and can be located remotely.

Addtionally, you can achieve cooldown quicker with a pumped, circulating system.

Tell us more about your process, liquid and th cooldown time.

My opinion only.......

-MJC

  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources