What determines the size of LV cables on a Transformer ?
Say on a 11000/415 volt 800 kVA, is it the conected load or the the actual kVA Rating?

RE: Size of LV cables of a Transformer

2
i always size the cable on the LV side of the transformer based on KVA rating and not on the connected load..

i always consider the future load growth which will be a problem if you size the cable on the present connected load only...


dydt

RE: Size of LV cables of a Transformer

(OP)
Dear dydt,

Many thanks for that answer, it was the answer I was hoping for.
I have read several books but cannot find a hard and fast answer to my question.
I was not sure if short circuit current came into the equation, but I shall use your solution.

Again many thanks,

Paul

RE: Size of LV cables of a Transformer

Paul,
I aggree with DYDT. Size to KVA rating.

RE: Size of LV cables of a Transformer

the short circuit rating will come into play when you select the protection settings.

RE: Size of LV cables of a Transformer

Consistent with views already stated, why would you want to restrict transformer loading via secondary bus/conductor sizing?  In most cases, that would seem like a false sense of economy.

RE: Size of LV cables of a Transformer

Hi,

Yep KVA it is!

Just keep in mind that laying conditions will affect current carrying capacity.

best of luck..

ADN

RE: Size of LV cables of a Transformer

Since we are on the subject:  What protects the cable on the secondary side???  Would it be the breaker on the HV side???  

Wirenut

RE: Size of LV cables of a Transformer

The main breaker or fuse your terminating your low voltage cable at, for overloads, and the primary and secondary protection for short circuits.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources