Short Circuit MVA values.
Short Circuit MVA values.
(OP)
When the taps of a transformer are raised (or lowered), does the available short circuit MVA at the transformer secondary raise (or lower) or stay the same as calculated at nominal tap settings?
Raisinbran
Raisinbran






RE: Short Circuit MVA values.
A couple test examples:
12 MVA 100-12.47 kV transformer:
105 kV tap - 8.84%
102.5 kV tap - 8.84%
100 kV tap - 8.87%
97.5 kV tap - 8.97%
95 kV tap - 9.12%
15 MVA 100-12.47 kV transformer:
105 kV tap - 9.18%
102.5 kV tap - 9.10%
100 kV tap - 9.08%
97.5 kV tap - 9.13%
95 kV tap - 9.22%