VFD sizing for a range of motor sizes
Can a VFD rated for a 184 kW motor successfully operate a motor with a much smaller rating, say 55 kW? I'm working on a project which would require VFD control for the sewage pump motors. Initially, 55 kW pumps would be installed but these would be scheduled for replacement with 184 kW after about 11 years operation when facility requirements would be higher. I intend to design for the utlimate capacity rather than for the initial size since replacing the VFD later would also be very expensive.
RE: VFD sizing for a range of motor sizes
Especially if it is a scalar drive - and a pump drive usually is.
The only thing that I can think of is: Can the thermal protection be set for the smaller motor? That is normally not a problem.
If you think that a vector drive is necessary (can't see why) then you may need to check to make sure that the R:s and X:s (resistances and impedances) of the smaller motor are civered by the parameters in the drive. Again, with a 1:4 ratio between motor and inverter, that should not be a problem at all.
There might be a physical problem with the cabling. A cable for a 184 kW motor may be a problem to connect to a 55 kW motor. But that is solvable, just put a junction box close to the small motor and connect with a smaller area from there. Remember to fuse accordingly!
Gunnar Englund
www.gke.org
Eng-Tips: Help for your job, not for your homework Read FAQ731-376
Gunnar Englund
www.gke.org
We may also be faced with requirements for low harmonic drives which wil require active rectifiers or similar.
Best regards
Mark Empson
http://www.lmphotonics.com
One day my ship will come in.
But with my luck, I'll be at the airport!
Gunnar Englund
www.gke.org
If that hadn't come from you, I don't think I would have interpreted it as a complment!
Mark,
Matrix drives, good point. The technology is expensive now, but basic PWM drives were comparitively expensive 11 years ago and look at them now. That is likely the wave of the future that far out.