I would like to know what is the effect of over dose and under dose of glycol in the cooling system.Is there any effect if the existing glycol will be mixed with different gycol such as frost gycol.





RE: Glycol content in Cooling system
Regards
Dave
RE: Glycol content in Cooling system
h
RE: Glycol content in Cooling system
RE: Glycol content in Cooling system
I agree to 50% is ideal for freeze protection. Unless the pipes are actually being designed to work outside we usually specify a 30-35% concentration as this will provide 'burst' protection down to -36F or so.
RE: Glycol content in Cooling system
60/40 is the max we have ever used in Arctic applications.
RE: Glycol content in Cooling system
Mixing glycols may or may not be a problem. It is best not to do it.
= = = = = = = = = = = = = = = = = = = =