W30 column unbraced lengths?

W30 column unbraced lengths?

W30 column unbraced lengths?

(OP)
Existing one story building, full diaphragm at roof from metal deck and horiz bracing, some column lines have vertical bracing, others have CMU wall tied into steel columns.  Question is: on outer column line there are W30x124 columns that have full height CMU walls (shear wall assuming) tied into web of columns with straps every 24", inside face of wall is 22 inches from inside flange of column, wall is 20 inches thick.  At the roof in the columns major axis a 4.5 feet deep truss that spans 45 ft frames into the column flange, truss chords WT12x55 T & B.
Can KLy be taken that minor axis is continuosly laterally braced, no sidesway, Ly=0 ?; can KLx be taken as 1.0 times height to underside of truss.

RE: W30 column unbraced lengths?

20" thick CMU?  Don't follow your description as to what the main, structural portion of the wall is.  Please expand a bit.  Thanks.

RE: W30 column unbraced lengths?

(OP)
3 wythes thick, 12 inch CMU in middle, a four inch thick veneer on inside and outside face according to drawing

RE: W30 column unbraced lengths?

The Kx would depend upon how the trusses are connected to the column. Do the columns and trusses work together as lateral frames to resist lateral loads?

I would normally not count on the masonry ties to provide bracing in the y direction.

RE: W30 column unbraced lengths?

jike is right - I would consider the CMU to brace in the Y direction only if I had confidence that the wall to column connections were strong enough to resist some level of tension/compression - say 2% of the axial load of the column.  Strap ties to CMU just don't "feel" reliable to me and someday the owner may remove a wall or two with an addition, etc.

If the truss to column connection is intended to work as a moment frame, then the kx would be 2.0.  Assuming that the base is assumed pinned.

RE: W30 column unbraced lengths?

I would not consider the column braced in the y direction for a different reason--the inside flange is too far (22") from the inside face of the masonry.

DaveAtkins

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources