Hi All,

I'd like to know if a circuit protected by a GFCI breaker is required to have a ground wire.

thanks,

yigo

RE: GFCI circuit

See NEC section 210-8(d).  It says that it can be
done, but the receptacle must be marked
"No Equipment Ground" and "GFCI Protected", and
the equipment grounding conductor cannot be
connected to any equipment or circuitry.
<als>
 

RE: GFCI circuit

Remember that the only time you can install a GFCI without an equipment grounding condcutor is when you are replacing a two wire receptacle.  All other applications will require an equipment grounding conductor.
Don

RE: GFCI circuit

(OP)
Fsmyth, I cannot find the reference in NEC 2002.Please be more specific, what  you mean by it can be done. In my understanding your statement is in conflict with Resqcapt19's one.

thanks

yigo

RE: GFCI circuit

It is now in 406.3(D), specifically 406.3(D)(3)(b) permits the use of a 3-wire GFCI as the replacement for an EXISTING 2-wire receptacle where grounding does not exist in the receptacle enclosure.  There are no provisions for NEW ungrounded receptacle installations.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources