(OP)
i need to know what is the meaning of ( limit output=200VA ) written on the name plate of a potential transfomer of 6600/100 volt ratio, with a rated output of ( 30 VA ) this pt is single phase class=0.5 transformer.

RE: pt limit output VA meaning

I would guess this is the thermal burden rating, meaning that it can put out up to 200 VA without overheating. However, once 30 VA is exceeded, it will no longer meet the 0.5 accuracy class.

RE: pt limit output VA meaning

(OP)
Dear scottf
in another pt name palte with two output coils of
(( 6600/square root(3),100/(sqare root(3),100/3 )) ratio, i read these data:

outlet terminal marking:  a,n       :     da,dn
rated output (VA)      :   30       :       50
accuracy class         :   0.5      :       6P
----------------------------------------------------
limit output           :          200 (VA)

now we have a two coils of 30&50 VA but also one limit output of 200 VA
could this limit output has a relation to the fuse connected to the input of potential transformer

thank you very much for any replay

RE: pt limit output VA meaning

bjeservice,

It would be impractical - nearly impossible - to provide a primary fuse at 6.6kV which would limit the input to 200VA. Such fuses don't simply exist as far as I know.

----------------------------------

One day my ship will come in.
But with my luck, I'll be at the airport!

RE: pt limit output VA meaning

bjeservice-

I agree with ScottyUK. The 200 VA, as you listed, just about has to be the thermal burden rating, which is to be considered total between the 2 windings.

In reality, I would suspect that the real thermal burden rating is much higher, but as you listed the nameplate data, that is about the only thing it could be.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources