Telecommunications Building - Current Harmonics
Telecommunications Building - Current Harmonics
(OP)
Hello All....
A power quality analysis was completed at my workplace (telecommunications building). The final report suggests that we have high levels of current harmonics in our power system (measured at the main service entrance switchboard). It also notes that the level of voltage harmonics is within IEEE standards. The consultant is suggesting that further power quality testing be carried out at individual loads to identify specific harmonic producing equipment.
It it correct to assume that SCR based rectifiers have a tendency to pollute the load side with voltage harmonics and AC side with current harmonics ?
If this assumption is correct, these finding make sense as there are no filters currently in place on the AC side of these rectifiers and since all DC equipment is backed up via large DC batteries (which act as filters), our electronic equipment have had no problems.
I'd like to know if any one has encountered similar problems and if limiting the current harmonics produced by AC-DC converters via filters helped there situation.
Thanks in advance
A power quality analysis was completed at my workplace (telecommunications building). The final report suggests that we have high levels of current harmonics in our power system (measured at the main service entrance switchboard). It also notes that the level of voltage harmonics is within IEEE standards. The consultant is suggesting that further power quality testing be carried out at individual loads to identify specific harmonic producing equipment.
It it correct to assume that SCR based rectifiers have a tendency to pollute the load side with voltage harmonics and AC side with current harmonics ?
If this assumption is correct, these finding make sense as there are no filters currently in place on the AC side of these rectifiers and since all DC equipment is backed up via large DC batteries (which act as filters), our electronic equipment have had no problems.
I'd like to know if any one has encountered similar problems and if limiting the current harmonics produced by AC-DC converters via filters helped there situation.
Thanks in advance






RE: Telecommunications Building - Current Harmonics
If you reduce the current harmonics caused by the non-linear power supplies, the current and voltage distortion will go down.
The first question to ask is whether or not these harmonic levels are creating any actual problems? Or is the serving utility complaining about harmonics (unlikely if your voltage distortion is within IEEE 519 limits).
There are a lot of people out there trying to sell solutions to power quality "problems" that are not really causing any real problems.
RE: Telecommunications Building - Current Harmonics
RE: Telecommunications Building - Current Harmonics
-> maximum voltage total harmonic distortion is typically less than 4% (with occasional spikes of 6-8%).
-> maximum current total harmonic distortion is typically between 10-15% (with occasional spikes of 18-25%).
RE: Telecommunications Building - Current Harmonics
On the other hand, the voltage distortion is rather high. As a rule, the voltage distortion is about ten times lower than current distortion (yes, can be twenty times lower too, depends on mains impedance/short circuit rating).
To me, it seems that your mains impedance is very high - or that the current distortion measurement is wrong.
Anyhow, the voltage distortion (4 percent) shall not be a problem at all.
Gunnar Englund
www.gke.org
RE: Telecommunications Building - Current Harmonics
For reference purposes, below is a sample of voltage and current distortion that I found in the net with uncompensated load harmonic data as follow:
Harmonic Voltage Current
Number Distortion [%] Distortion [%]
3rd 0.14 3.85
5th 3.85 15.21
7th 1.02 3.87
11th 1.22 4.41
THD 4.24 16.51