Bump Testing
Bump Testing
What are the requirements to bump test a Meduim Voltage Motor directly coupled to a reciprocating compressor?
Does one need to have all the utilies operational, cooling water, air, lube oil, (flushed) ???
An answer in the simplest form would be appreciated, required for planning purposes.
Thanks in advance.
Thanks in advance.
RE: Bump Testing
RE: Bump Testing
RE: Bump Testing
You could probably get away with running without cooling water for a few minutes. If you do not have the outlet connected, unload the discharge valves or remove the discharge valve assemblies you should be able to run it even longer.
Barry1961
RE: Bump Testing
To get pragmatic though
The bump test is generally done to ensure you got phase rotation on the motor correct ie motor turns the right direction. After this we generally put it on line and if ran OK put it in service.
SO the answer is yes you should have the thing ready to go in all respects before bump test.
Dan Bentler
RE: Bump Testing
"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla
Member, P3
stardelta (Mechanical)
Why the need to bump test is it just to determine rotation? Can you find someone who owns one of these, or beg/borrow/steal one and eliminate all the effort and risk?
ttp://www. fluke.co.u k/comx/sho w_product. aspx?local e=uken& ;pid=35297
jraef (Electrical)
stardelta,
Read the Eng-Tips Site Policies at FAQ731-376
RE: Bump Testing
h
RE: Bump Testing
I believe that device, and ones like it, are used to tell you what direction the motor is spinning while already running. You hook up the device to the motor, you bump it, and it tells you which direction it is spinning. It does not tell you which direction it is GOING to spin when you first hook it up. Only a bump test will tell you that. If you can't see a shaft during the bump test, these are very usefull. I've been trying to get sumersible pump people to use these on the pumps above ground before dropping them because once they are under water, you can't tell rotation directiona any longer except by flow differences.
Member, P3
aolalde (Electrical)
Hello JonnyWill.
abcd3286 (Electrical)
I don't know about the test unit from Fluke - never used it.
Appologies for my earlier comment which in retrospect was very vague. It can done with a suitable phase rotation indicator without having to power up the motor. We use an old but very reliable and easy to use instrument made by Biddle. Firstly the instrument is connected to the motor, The three leads from the Biddle are marked U V W and they must be connected to the corresponding phase circuits of the motor. The motor is lightly spun in a clockwise direction at the shaft. The biddle will then indicate phase rotation of the winding via a center reading meter, if it is also clockwise the phases are correctly marked for clockwise rotation at the shaft end with U/red V/yellow W/blue. If the biddle indicates anti-clockwise it will rotate anti-clockwise if fed U/red V/yellow W/blue. It is a requirement of IEC standards that motors rotate clockwise at the shaft end when fed U/red V/yellow W/Blue. We see many that have been rewound without phase direction being determined and the leads have marked wrongly as a result. The only downside is that the motor must be lightly spun by hand, not always possible if it is in situ. The link shows the latest version of the instrument we use.
RE: Bump Testing
A “Bump Test” is made to find the “Resonant Frequencies” or “Natural Frequencies” of a system.
If you want to analyze the motor alone, it will be uncoupled and excited by an impact, like “ringing a bell”. The whole vibration spectrum is recorded and the peak vibration found will identify the natural frequencies. If the system; motor- load- base is analyzed, do not uncouple the driven machine.
The motor and/or system do not need to rotate and I will leave the lubricants, cooling water etc close to the operating quantities since their mass could affect the results.
The most important result of this test is to show that the operating or forced exciting frequencies are far apart of the natural frequencies.
RE: Bump Testing
I have used Ideal (?) and I believe Greenlee has version also. Have two parts
one is same old phase rotation for supply conductors that has been used for eons. once you know phase rotation of supply the neat part (the second unit) comes in.
It can be hooked to motor leads then hand spin motor in desired rotation direction and this unit will tell you phase rotation of motor leads itself. Now all you have to do is match motor leads to supply leads and it should go right direction.
Pretty slick BUT be careful of which end you referance to -0 you GOTTA read the directions.
Dan Bentler
RE: Bump Testing
http://www.inotek.com/Catalog/biddle2pm.html